supportadmin Posted November 17, 2022 Posted November 17, 2022 1. How to calibrate Shelly 3EM with a neutral CT? Update the shelly 3EM device to fw 1.12, where the functionality for neutral CT is supported. 1. Lock N to phase A, don't unlock A clamp. 2. Choose to calibrate N from A 3. If callibration fails, reverse N and try again. 4. When is successful move N clamp to Neutral wire. 2. How to interpret the readings for A+B+C RMS and Neutral RMS? It is important to take in mind the error from the equipment. A small difference between 0.5 A and 1A could be taken for normal. Higher difference could mean leakage in the electrical network.