TB93 Posted November 11 Posted November 11 Hello, I use my shelly in a 3x230v configuration. The relay works but the input not. When nothing is connected to the input I measure a voltage of aprox 73V on the input. What is wrong here? Quote Translate Revert translation? English (American) Finnish French German Italian Portuguese (European) Spanish
Members thgoebel Posted November 11 Members Posted November 11 (edited) How did you wire the Shelly? Please attach a sketch or a picture! The measured voltage is quite normal, due to the fact the input should be activated both with live an neutral potential. Did you measure the voltage between SW and N? Do you have an articulated neutral wire or three lives only? Edited November 11 by thgoebel Quote Translate Revert translation? English (American) Finnish French German Italian Portuguese (European) Spanish
If_then_else Posted November 11 Posted November 11 (edited) Can you carry out 2 x 2 measurements, once with the contact on the input open and once closed: Shelly "L" <> Shelly "Input" Shelly "N" <> Shelly "Input" Your designation 3x230V makes me suspect that you are talking about a three phase / tree wire system, can you confirm this? Possibly with the corresponding number as shown below. Edited November 11 by If_then_else Quote Translate Revert translation? English (American) Finnish French German Italian Portuguese (European) Spanish