Hello everyone,

I have a technical question, as I'm not very familiar with electrical engineering:
the Shelly 1 PM Mini Gen 3 has a max. switching current of 8 A.
It is always said that you should check that the cables are fused accordingly. I looked in the switch box and everything there is fused with 16A. Now I'm wondering: Can I use the Shelle 1 PM Mini Gen 3 as it only goes up to 8 A?

 

And am I right in thinking that using the Shelly PM Mini Gen 3 with its 16 A is not a problem?

 

Regards,

Doktor

Posted (edited)

16 A is a standard for cabling. what you have to care is that the current that pass through the shelly is no more than 8 A, and normally you know, it is written on the devices .
Anyway on the shelly tehre is among the setting als "protection" where you may set a limit of 7.5A so if it is exceeded the relay would promptly disengage. to be even safer add also an 8 A fuse ahead.

Edited by wooly
Posted

correct there are safety settings on the device that will stop the current from pulling more than it should its not so much to have the circuit breaker trip before the device does. Main thing is to not have a surge of over current pass through the device eg a pool pump for a mini that will never survive and not built for that 

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Unfortunately, your content contains terms that we do not allow. Please edit your content to remove the highlighted words below.
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...