I'm having a problem reading active power with the PRO EM-50. If the cos phi is very close to 0, the power reading is completely wrong. On the other hand, with the PRO 3EM, still in single phase, the power reading remains correct. In my case, my heat pump was stopped :
- Active power: 16W
- Apparent power: 350VA
- Amperage: 1.46A

The EM-50 and 3EM measured the same current and voltage. However, the 3EM didn't calculate the phase shift correctly. As a result, the EM-50 is nowhere near the 2% accuracy between 0 and 1 amp that it claims. Is my model the problem? Is there a specific adjustment I need to make? Why is the 3EM calculating active power correctly? When the cos phi is better, the EM-50 and 3EM have relatively consistent readings, for example for my hot water tank :
- Active power: 18W
- Apparent power: 48VA

- Amperage: 0.2A

--------------------------------------------------------------------------
J’ai un problème de relevé de la puissance active avec le PRO EM-50. Si le cos phi est très proche de 0, le relevé de la puissance est totalement faux. Alors qu’avec le PRO 3EM toujours en monophasé, le relevé de la puissance reste juste. Dans mon cas de figure, j’avais pour ma pompe à chaleur à l’arrêt :
-          Puissance active : 16W
-          Puissance apparente : 350VA
-          Ampérage : 1,46A

Le EM-50 et 3EM mesurait bien le même ampérage et tension. Par contre, le 3EM ne calculait pas de déphasage comme il faut. Du coup, le EM-50 est très loin des 2% de précision entre 0 et 1 A comme indiqué. Est-ce que c’est mon modèle qui a un problème ? Est-ce qu’il y a un réglage particulier à faire ? Pourquoi le 3EM calcul correctement la puissance active ? Lorsque le cos phi est meilleurs, le EM-50 et 3EM ont des mesures relativement cohérentes, par exemple pour mon ballon d’eau chaude :
-          Puissance active : 18W
-          Puissance apparente : 48VA
-          Ampérage : 0,2A

Link to comment
Share on other sites

And even with a cos phi close to 1, the EM-50 still has a significant margin of error, while the 3EM is accurate compared to the value measured by Victron. I'm using the latest 1.4.3 firmware on both units. What do I need to do to get the EM-50 to give me an accurate result ?

--------------------------------------------------------------------------

Et même avec un cos phi proche de 1, EM-50 a une marge d'erreur encore non négligeable alors que le 3EM est lui exacte si on le compare avec la valeur mesurée par Victron. Je suis sur le dernier Firmware 1.4.3 sur les 2 appareils. Que dois-je faire pour que EM-50 me donne un résultat exacte ?

Pro 3EM.jpg

Pro EM-50.jpg

Victron.jpg

Link to comment
Share on other sites

  • Members

Sometimes the specs have to be read thoroughly. For the Shelly pro EM-50, an accuracy of 1% for the voltage measurement and 2% for the current measurement is indicated:

IMG_1510.thumb.jpeg.12c7e7f5764402bc828ce773425b0886.jpeg
 

Power is U * I * cosφ. Thus, the both accuracies have to (geometrically) added. This gives more than 1% accuracy.

Furthermore, you‘re comparing Shelly pro EM-50 with Shelly pro 3EM. Accuracy for Shelly pro 3EM is 1% for voltage measurement and 5% max. for current measurement:

IMG_1511.thumb.jpeg.c618ef1da3fc661257ddb1c992712a48.jpeg

Hence, your reference device is less precise as your device under test! For power measurement accuracy, the same as above written is valid.

Conclusion: 3,4% deviation with power measurement is lamentable but a common fact.

Edited by thgoebel
Link to comment
Share on other sites

Indeed, thank you for these clarifications, you're right.

Having said that, I also tried with my Legrand eco-meter and the value was also accurate compared to the 3EM and Victron, whether in the case of 6000W or 18W. So I'm wondering if my EM-50 has a bad calibration.

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...