malonip

Recommended Posts

Hello,
I am a bit perplex and look for help in understanding what could be wrong.

I am trying to measure power (and energy) values of my heatpump (PAC pompe à chaleur, in French) - triphased - with a Shelly Pro 3EM-120. I wired it upstream of the 3-phase input to the heat pump (electric current up > down, there is another (main) electrical cabinet above it). Like this :

image.thumb.png.5acddd3693eb340dc4163b91ce6c0368.png

When the heatpump is in a "standby" mode or just make run a circulating pump, the power values from the Shelly seem to be completely fine (around 10W, up to 30W when the solar circulation pump is running - see screenshot) :

image.thumb.png.644847e97a16db6f594d9ae9fdf235ea.png

But as soon as the heatpump starts "big activity", such producing hot water, which usually consumes around 2500 W, I am getting negative and mad values from the Shelly Pro :

image.thumb.png.78a280dd877a9142b2348162ab50a3f2.png

On my Home Assistant dashboard, the problem is clear :

image.png.b081dc9e414ce245538d8e2caff87465.png

Globally the house consumes 3.3 kW. 500-600W is standard stuff, so the heatpump should show something around 2500W usage, and not this -223W negative values.

As soon as the heatpump stops to need high power, normal power values get back, as explained above.

As shown in the Home Assistant screenshot above, my global electric installation use solar panels (Enphase). Could the negative values be linked to this and how can I correct the Shelly power values ? Or should I connect the Shelly Pro to other phase locations ? (or is it an hardware issue, very unlikely because hardware is new ?).

Thanks for your ideas...

PS : curiously, the clamps are supposed to be in the correct direction (K->L, up->down), but I had to invert the values in the Shelly interface for displaying the "correct" low W values, when the heatpump is in standby mode. This explains perhaps partially negative values when the heatpump is at max power.

 

Pierre

 

image.png

Link to comment
Share on other sites

Hi @thgoebel,

This is clearly not the case : the Shelly Pro is connected "further down", after a circuit breaker.

image.thumb.png.3c9b93a2452e81a62444e148f84a5acf.png

Is it necessary that it must be connected to the same wire the clamp is connected to ? I thought it didn't matter (because we are just measuring a magnetic current passing through the clamp). If yes, so I need to connect it in another location.

Thanks a lot for your help !

 

Link to comment
Share on other sites

  • Members
1 hour ago, malonip said:

? I thought it didn't matter (because we are just measuring a magnetic current passing through the clamp).

It does matter, indeed! This is because power measurement in AC systems needs the knowledge of the phase shift between voltage and current. Formula is P = U * I * cos φ, where P is power, I is current and φ the phase shift between current and voltage. If you interchange two phases, the phase shift is misaligned, thus showing erroneous power values.

Edited by thgoebel
Link to comment
Share on other sites

Thanks a lot, @thgoebel !
The phases were fine, but 
I've connected the Shelly PRO to other wires (under the circuit breaker 2), with the clamps measuring the same wires where the Shelly PRO is connected to, and now I am getting correct values !

Again, thanks a lot !

 

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...