Hi there, 

I have a heating rod in my warn water boiler that is switched from HA when photovoltaic has power left over. The heating rod is 3KW, so max. 14A given 230-240 V we are having here.

The Shelly Plug should support 16A continuous draw? Nevertheless it's the second Shelly that melted. After the first I changes also the power socket to be more robust.

Please see the picture.

What wife switch would you recommend instead? And could I get a refund for it?

 

Best

David

IMG_20240907_132830_418.jpg

  • Members
Posted (edited)

Two possible issues:

(a) The contact pin of the Shelly got too hot (by whatsoever reason) and melted the power socket, or

(b) contact resistance in the power socket was to high, which heated the contact pin up and melted the Shelly‘s case.

What rated power and current has the power socket, please?

There is some evidence for a contact resistance at the pin, which may be caused by a slacked contact in the socket:

IMG_1442.thumb.jpeg.05315e75d4269ab2ede159f5434a565d.jpeg

Edited by thgoebel
Posted

Hi, the socket is rated 16A as well.

 

A friend mentioned yesterday that perhaps the relais was switching on/off too often? 

But that shouldn't actually matter? 

Also as it's a resistive load there is no such thing as starting current, right?

 

I'll survive the loss of that shelly switch! 

What could I potentially do to avoid this? Shelly without sockets and direct cable clamp?

Posted (edited)

Dauerlasten in dieser Höhe schaltet man per Schütz und nicht per Plug da die Steckdose in der Regel nur für 60min geprüft ist! Das mech. Kontaktproblem hat Thomas schon erwähnt. Damit ist Shelly nicht alleine.

 

Eine Plus in normalen UP Dose würde ich auch nicht empfehlen da du die Abwärme nicht weg bringst.

Edited by AlexAn
Posted

Writing in English again, maybe some more people might want to know?

This seems to work just fine. Now waiting for the sun so we get power for "free"!

 

One question though: As per datasheet the shelly 1 mini gen3 should have a temp sensor built in?

image.png.831f842dfb51751ff635d484dba3a429.png

Seems the entity can't be added anywhere though?

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Unfortunately, your content contains terms that we do not allow. Please edit your content to remove the highlighted words below.
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...