Jump to content
Visit us at IFA2024 / Besuche uns auf der IFA2024 06.-10.09.2024 Stand H1.2-420 ×
Shelly wiring diagram Now LIVE ×

Total Energy values wrongly summed


jwefers

Recommended Posts

Until now, i pulled my power and energy values directly from our (german) grid meter.

At least in Germany, the meter calculates the energy values from the power sums over all three phases. E.g. you pull 50W from phase A and push 25W each on B and C - counters do not move (for both import and export).

 

The Pro 3 EM however seems to calculate the sum as the sum of the three separate phase counters, i.e. in the above scenario, after an hour, i get 50Wh imported and 50Wh exported.

 

This means this build-in total energy counter is useless if you have mixed positive/negative power values.

 

Am i getting this wrong? Is there a hidden setting to fix this?

 

Do i really have to make my own counter as the integral over the sum the power values?

Edited by jwefers
miscalculate
Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...