In the wiring diagram that came with the Shelly, the cables to power it tap that power before the CT clamps I guess meaning that the Shelly is not considered part of the load.

That makes installation in my case much more complicated since it means I would have to split the 3 phase cables before the main breaker.

So, can the CTs be put just before the main breaker and power for the meter (A,B,C) at some point after it ?

Also are 10A breakers for A,B,C OK ? The installation doesn't specify an appropriate breaker size.

Thanks for any info!

  • Members
Posted
22 minutes ago, PentVaer said:

So, can the CTs be put just before the main breaker and power for the meter (A,B,C) at some point after it ?

This is possible. 
 

Due to the fact, the Shelly pro 3EM is consuming very small power, I would suggest to use micro fuses with 300 to 500mA in fuse-holders:

Click

This measure protects the Shelly itself. A possible fault shall not cause massive damage. Thus, the device may be repaired…

Posted

Terrific, thanks for the quick help.

 

1 hour ago, thgoebel said:

This is possible. 
 

Due to the fact, the Shelly pro 3EM is consuming very small power, I would suggest to use micro fuses with 300 to 500mA in fuse-holders:

Click

This measure protects the Shelly itself. A possible fault shall not cause massive damage. Thus, the device may be repaired…

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Erstelle neue...